1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Utility Breaker Clearing Time

Discussion in 'System Modeling and Calculations' started by mountaineer, Jul 22, 2010.

  1. mountaineer Member

    Just had to model my first job where there was no overcurrent protection at the utility pole. The station is close to the utility substation and the line is being protected by relays at the substation. The modeling software goes into specific detail in defining the breaker. What realistically do I need from the utility to model - # of cycle clearing time? Is there a standard for different voltage levels? If the breaker was part of my analysis I would need all the details but I don't want to be asking for info and having them jump through hoops for info I don't really need.

    Thanks for your help.
  2. acobb Well-Known Member

    Source r+jx values, breaker rated interupting time, CT tap and OC relay settings, reclosing times, wire size and length, transformer %Z. Surprising that there is no high side protection unless it is a dedicated feeder to the plant.
  3. mountaineer Member

    The utility said there are only a few installations where there is no pole mounted protection. It only occurs when the station is very close to the substation - it's an old service.

    I have pretty much everything you listed. How are the reclosing times used? The utility offered them and I see no mention of using them in the software. Thanks for any help.
  4. acobb Well-Known Member

    We usually try to make sure the breaker is on non-reclose when live maintenance is performed. Will be difficult in your case. The only issue is when/if one of your employees makes a mistake ahead of your OCPD. Many utilities operate distribution circuits with the first reclose cycle initiated as soon as the breaker opens.....no intentional time delay involved. Subsequent reclose cycles mey be as long as 10 to 30 seconds.

    If you get an immediate reclose after the first trip of the utility breaker, the question is will the arc restrike?
    Has the problem cleared?
    Will the worker be clear?
    Do we have a second event of some sort?

    Is there a high side switch? You could always get the utility to kill it if you need to work on the main.

    Hence my preference for the non-reclose.
  5. mountaineer Member

    Thank you for the explanation. This would definitely be an issue on the line side of the main service breaker for county personnel. The software doesn't account for it but it needs to be pointed out to the customer. Is that a true statement?
  6. acobb Well-Known Member

    Sorry for taking so long to get back....yes it does need to be pointed out and depending on the IE level you might want to make sure it is not worked energized.