Calculations for 208v System

Discussion in 'General Discussion' started by mountaineer, Jul 22, 2010.

  1. mountaineer Sparks Level

    I have read about the exemption for <240V and <125kva transformer. Also have read about the accuracy of each calculation method for different voltage levels. I have come across a situation where the transformer is 225kva, 12kv to 208v for a small pumping station. Which calculation method is most accurate for this? Turns out the 225 kva transformer is large because it feeds a variety of other loads in addition to the substation. The utility has given me a transformer fault current of 28,400A for the secondary side.

    Typically the transformers are fairly small, dedicated to the load and the secondary voltage higher.

    I appreciate any comments.
  2. JBD Sparks Level

    We use the 'standard' IEEE 1584 calculations for 208V systems.