1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Overdutied Device Interrupting Ratings

Discussion in 'System Modeling and Calculations' started by jkopinski, Jul 15, 2010.

  1. jkopinski New Member

    NFPA 70E says that "design" and "condition of maintenance" should be taken into account for arc flash hazard analysis.

    For equipment with over-dutied interrupting ratings what is the proper approach for an arc flash hazard analysis? As in what was the intention of NFPA in incorporating design, or lack thereof, into the analysis?
  2. Zog Well-Known Member

    I suume you mean your available fault current is > the AIC rating of your breaker? If so I would not assume that breaker is an OCPD at all.

    The 70E is not a design or instalation standard, that is what the NFPA 70 is for (NEC).

    Good question, interested to see what others do in this case.
  3. acobb Well-Known Member

    If you cannot find an acceptable method to lower the available fault duty, then I would replace the equipment while there is still something to replace.
  4. cbauer Well-Known Member

    NFPA 70 should not be considered a "design standard". I would classify it more as a "minimum requirememnts installation guide".