1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Available fault currents and under rated equipment

Discussion in 'Arc Flash Labels' started by will40, Jun 11, 2010.

  1. will40 New Member

    This might be a stupid question but I want to cover any exceptions to something that is quite clear to me as a problem.

    We had a SC/AF study performed for a customer of ours by an engineering firm. During the equipment labeling phase we confirm the equipment is rated for the calculated fault current that is available as we affix each label.

    The customer's 480V 2500A bus duct riser has fault current upward of 60-70KAIC calculated on the floors. We discovered many of the fused bus duct disconnects serving Siemens S2 480V panel boards with ED4 circuit breakers have NOS 200A (one time fuses) rated for 10KAIC.

    To me this is an issue. My solution would be to install current liminting J fuses in the disconnects and they would series rate with the ED4 breakers and problems would be solved.

    Before I make this solution suggestion are there any exceptions I am not aware of?

    If the 2500A Bus Duct riser fuses are current limiting KRP-C, from what I understand the let through current is still greater than 10KAIC so to me this is still an issue with the bus duct switch fuses.

    Are our findings valid?

    Thanks for your help.
  2. cbauer Well-Known Member

    You will have to follow the quidelines in NEC article 240.86.
  3. will40 New Member

    240.86, A, B, and C noted.

    As well as 110.22.

    Thanks.

    Will