1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

LV CB operation

Discussion in 'Electrical Safety Practices' started by Barrusr, Jun 1, 2010.

  1. Barrusr New Member

    I'm not using tables because I've done my calculations. At a panelboard, I've determined Ie=0.6cal/cm2 and AF boundary in the neighborhood of 12".

    Can someone cite the code section which mandates any specific clothing requirements for the operation of a CB in this panelboard ?

    thanks
  2. brainfiller Administrator

    Check out:

    NFPA 70E - 2008 Edition 130.3(B)(1) Incident Energy Analysis

    Arc Rated FR clothing and other PPE shall be used by the employee based on the incident energy exposure...

    This is based on the incident energy at the working distance which is typically 18 inches. At 18 inches you seem to have a very low incident energy which would lead to PPE category 0 <1.2 cal.cm2

    It is also based on working within the Arc Flash Protection Boundary which for you is 12 inches.

    Your hands will likely need protection from arc flash since they will be closer and I prefer to wear FR clothing anyway. Once you have seen even a low level arc flash, it really gets your attention.