1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

208V low arc current long clearing time

Discussion in 'System Modeling and Calculations' started by alb, May 27, 2010.

  1. alb New Member

    I am reviewing an arc flash study with several low voltage (208) panelboards that have a low calculated arc current, less than 3000A, with long clearing times, 2 seconds or more. This is resulting in high energy and Cat #3 or #4 PPE. Are these calculations reasonable? Will that low a voltage and current even sustain an arc? Most of these currents are below the current calculated from a 112.5 kVA transformer which can be ignored at 208V. Any thoughts would be appreciated.

    Thanks
  2. brainfiller Administrator

    You will find numerous posts about this on the forum. Here is a short summary:

    The "less than 125 kVA" limit was initally used in IEEE 1584. Later, a few concerns arose about its validity. A few people (I'm one of them) have been involved in testing.

    It looks like eventually the cut off will be based on short circuit current not kVA and from what I have been involved with it will be much lower than the current from a 112.5 kVA transformer.

    I am now the task group leader for this with IEEE 1584 and it is formally being reviewed.

    You will find more detail throughout the forum.

    Good Luck, Let me know if you have any more questions.