1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

"... in its Immediate Power Supply"?

Discussion in 'IEEE 1584 - IEEE Guide for Performing Arc-Flash Ha' started by mnmurphy, Apr 24, 2008.

  1. mnmurphy New Member

    What do you think qualifies as immediate power supply?

    I notice in some programs, for anything below 240V it means the nearest upstream transformer, even if it is a few panels up.

    This is in reference to IEEE 1584, p6, where it says, "equipment below 240V need not be considered unless it involves at least one 125kVA or larger low-impedance transformer in its immediate power supply." Immediate is nowhere defined in the standard, and I am not sure I have seen it defined in any other common standards.

    :confused:
  2. WDeanN Well-Known Member

    Not sure what the intent was, but I usually cut it off at the first panel, unless the next level is fed by a large breaker / wiring.
    I would make this call based on the previous part of the sentence: "...low-impedance transformer..."

    Any smaller sized wiring leading to the downstream panels may have enough impedence to qualify, and reduce the hazard significantly.

    What the cutoff is, I don't have any idea. I look at them case by case.

    I know, not much help. I thought you guys were working on a study standard to clarify this stuff?