1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Transformers smaller than 125KVA, 208V

Discussion in 'System Modeling and Calculations' started by PA Sparky, Jul 8, 2007.

  1. PA Sparky New Member

    Should an arc flash study be performed on 208V systems fed by transformers smaller than 125KVA? IEEE 1584 indicates an arc-flash hazard should not be a concern. NFPA 70E specifically does not address this issue.
  2. Boxer23 New Member

    I think the idea is that the fault current would be low enough on the secondary of small transformers that it is not considered a severe threat. We don't review the system beyond the small transformers for that reason. I am sure some will review everything but many stop at the small transformers. You are correct that this is not covered in 70E. 70E requires a flash hazard analysis that could involve using the hazard risk tables and simple flash boundary formulas or it could involve detailed calculations but they don't say how to conduct the calculations so you rely in 1584.
  3. ARC_Dave Member

    208 circuits

    IAW the IEEE 1584, the cutoff is 208VAC systems fed by transformers that are below 112.5KVA. They aren't required to be calculated, because a fault on their secondary would be so small as to be classified as a "non-event". The do however, have to be labeled, if you follow the NEC 110.16 edict regarding labeling of components.
  4. Homerjs78 New Member

    This can come down to the fault current level. If the max fault current is under a few hundred amps, this is no more dangerous than a typical industrial welder.
  5. raffle New Member

    208 system, less 125kVA transformer

    For 208 system, less than 125 kVA transformer, you can use NFPA, table 130.7(c)(9)(a) because you will have less than 10kA short circuit current available=> can reduce hazard/ risk category by one number.


    This means you will end up with category 0 for 208V system.

    Raffle
  6. Gary B Well-Known Member

    We have been trying to sort this out in a 'least liable' way. Performing calculations in such instances has resulted in risk category 1 or lower, for our given parameters. We have not been able to get the results above that level.

    (at this particular site, they have decided to label all installations as requiring RC 1 PPE as a base level of protective PPE to enter the plant, so that has been the threshold we seek)