1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Does this make sense? If so, then how?

Discussion in 'General Discussion' started by titan, Apr 29, 2010.

  1. titan New Member

    If I have a 225kVA 4.16kv/480V xfmr in my model and I run arc-flash using ETAP.

    Is it possible that the high side gets a lower HRC than the secondary side?

    Let's say there is a 50E fuse on the primary side.

    The results come back as Cat 0 for the primary side and Cat 1 on the secondary side.

    I am hesistant to put a Cat 0 stick on the primary side. Is there something wrong with my calculations or is this normal? I have seen this in a few other studies as well.
  2. stevenal Well-Known Member

    Yes. Arc flash is current Dependant, and you have much less on the primary side.
  3. jghrist Well-Known Member

    And probably faster clearing.
  4. titan New Member

    I just found that to be kind of strange to have a low primary side but a really high secondary side when I am dealing with transformers in ETAP
  5. Zog Well-Known Member

    Normal to see that. A fault on the secondary side before the OCPD will rely on the primary fuses to clear the fault, but they will see much lower current levels on the other side of the transformer and have a long clearing time.
  6. titan New Member

    Wouldn't the current levels be higher?
  7. jghrist Well-Known Member

    Current level is inversely proportional to voltage level.
  8. JBD Well-Known Member

    Most people are surprised that the secondary AFIE is so high compared to the primary. This is the reason that service entrance locations are usually aove 40 cal/cm². And why the 'task table' should not be used for these locations.