1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Need recommendations

Discussion in 'General Discussion' started by bruinfan, Apr 24, 2010.

  1. bruinfan New Member

    I have a 3000kVA utility transformer with its secondary connected directly to the main switchgear bus. When I run the arc flash it produces an incident energy of 150 cal/cm^2. Any recommendations as to how I can lower that incident energy? With the transformer connected directly to the bus there doesn't appear to be a place to install a main circuit breaker or anything. I am kind of stumped on this one. Any help would be greatly appreciated.

    Thanks in advance!
  2. Zog Well-Known Member

    You have a common problem and thee are a few mitigation solutions, In fact I am presenting mitigation mitigation solutions at a conference in 2 hours on this very issue. First thing to look at is your primary fuse, there may be some older types that will work much better. If not you can replace your primary fuse with a mini VCB that uses current inputs from the secondary side of the transformer.

    Remote racking and switchnig may be the right solution too, depending on your needs.
  3. haze10 Well-Known Member

    I think S&C was making electronic fuses that have programable trip points. You could try to work in a CB on the primary but have the CTs on the secondary. Also, check the fuse catalogs to see if there is a faster one.
  4. ghostbuster New Member

    Here is a link to S/C fault fiter electronic fuse arrangement.I plugged this into our arc flash program and it reduced the main board from 170 cal to 48 cal.


    http://www.sandc.com/products/faultfiter/default.asp