1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

interrupting time poll

Discussion in 'System Modeling and Calculations' started by stevenal, Apr 5, 2010.

?

Based on IEEE C7.05 section 5.6, do you add an extra half or full cycle to your time?

Yes: I use 3.5 cycles for a 3 cycle breaker and 6 cycles for a 5 cycle breaker before adding relay t 1 vote(s) 14.3%
No: Rated breaker time plus relay time is sufficient. 3 vote(s) 42.9%
Depends on situation. 1 vote(s) 14.3%
Other 2 vote(s) 28.6%
  1. stevenal Well-Known Member

    No response to the first thread. Perhaps a poll will collect more?

    Based on IEEE C37.04 section 5.6, do you add an extra half or full cycle to to your breaker rating when figuring IE?
  2. jghrist Well-Known Member

    Maybe if you quoted the referenced section and the title of the standard. I can't find a C7.05 in browsing through IEEE Xplore. I also can't find a C37.05.
  3. Zog Well-Known Member

    I said other because we now try to base our studies of first trip data, not a table that says when it "should" trip.
  4. stevenal Well-Known Member

    Sorry, corrected in the body; but I see no way to correct the question.

    "5.6 Rated interrupting time
    The rated interrupting time of a circuit breaker is the maximum permissible interval between the energizing
    of the trip circuit at rated control voltage and rated operating pressure for mechanical operation, and the
    interruption of the current in the main circuit in all poles. The interrupting time for a close-open operation
    shall not exceed the rated interrupting time by more than 1 cycle of rated power frequency for circuit breakers
    with interrupting times of 5 cycles or more, and 1/2 cycle for circuit breakers with interrupting times of
    3 cycles or less. (Cycles are based on corresponding rated power frequency.)"

    Please note that the adder is for a CO operation. This is a close into fault situation.
  5. stevenal Well-Known Member

    Zog,

    Please explain. Where do you get "first trip data?"

    Breaker rated interrupting time is not used?

    I never suggested using a table.
  6. Zog Well-Known Member

    Table, software database, whatever, all the same, not real values. Not trying to pick on you though, most people are still doing it with published data. The future of accurate studies is first trip data. (Google it and you will see all the articles, gathering a lot of steam in the testing world).

    (The following is reposted from a NETA world article by my co-worker, Don Genutis)

    Typically, circuit breakers remain dormant for very long periods of time, but when called upon to interrupt a fault, they are expected to operate within finite times based upon their protective settings. These settings are derived by conducting coordination and arc-flash studies to optimize electrical system performance and enhance worker safety. Typically, the breaker’s lubrication conditioncchanges over time, due to a number of factors, and hardens to a point where the breaker’s first trip is inhibited. This first trip represents the breaker’s true operating time and often differs greatly from the values expected in the studies thus adversely affecting system performance and exposing the worker to higher levels of incident energy and making the studies invalid.

    The only solution to validate the studies and to protect the worker is to frequently verify breaker timing under first trip conditions. Typical maintenance and testing occurs after the breaker has already been tripped once, and thus the critical first trip condition information is lost. Regular exercising of the breaker can help the first trip performance. Frequent maintenance will also help, but these activities do not ensure optimum first trip operation.

    A new technology has evolved that efficiently determines breaker first trip performance thus enabling validation of the arc-flash study. This technology has the additional benefit of verifying overall breaker mechanical condition. A special transducer is magnetically coupled to the front of the breaker ,after the technician moves from the exposure zone, the breaker is operated. The
    transducer sends valuable vibration signals that represent breaker first trip timing and mechanical condition to a handheld analyzer. This unique breaker vibration signature is compared to a database library of known signatures.

    Post test analysis can include superimposing the test breaker signature upon good breaker signatures to quickly spot potential problems. Should the breaker fail the first trip test in the field, it is necessary to perform complete shop reconditioning or remanufacturing in order to return the breaker to a condition that will ensure proper operation and validate the arc-flash study. Frequent performance of the breaker vibration signature test ensures performance and exercises the breaker mechanism.

    Here is a link to the full article, http://www.nooutageelectricaltesting.com/PDF/no-outage-safety.pdf
  7. stevenal Well-Known Member

    Zog,

    Seems to be a verification of the breaker mechanical operating time. Not sure how you get from there to the interrupting time. A "first interrupting time" test would require a source capable of supplying rated interrupting current to the breaker. I think I'll leave that to the manufacturers. And we seem to be considering only an open after a long time closed, just the opposite of my suggestion to use the CO extra half or full cycle.
  8. Zog Well-Known Member

    You can have the fastest relay in the world but if the breaker will not open in the assumed time it does you no good. We simulate they fault curent via secondary injection with the breaker still in the cell. Primary injection can only be done after the breakr is removed from the cell and is still done to verify the CT's are operating correctly after the first trip data is recorded.

    First trip is the future of breaker testing and arc flash studies, stay tuned.
  9. stevenal Well-Known Member

    Zog,

    Secondary injection does not emulate the way primary fault current is cleared. You can have the fastest breaker mechanism in the world, and it will do you no good if the current continues to arc across the contacts for very long.

    And primary injection test sets cannot provide sufficient current/voltage to emulate a real fault.

    Clearing time = relay time + interrupting time.

    Interrupting time = opening time + arcing time.

    For an illustration see C37.010 Figure 2. I fear your method is neglecting the arcing time.
  10. jghrist Well-Known Member

    If I understand the standard correctly, the extra time would only apply when closing into a fault. In this case, the actual arcing time at the fault location will be less than the CO time of the breaker. Before the breaker is closed, there is no voltage at the fault location and no arcing. To close into a fault would mean that the fault would either be bolted to start with (no gap) or have a very small gap that would arc over after energization. It could develop into an arc across the assumed gap distance, but only after some finite time.

    I voted for using interrupting time plus relay time.
  11. Zog Well-Known Member


    Not at all, still factored in, but our method is finding the real opening time, not the assumed opening time.
  12. stevenal Well-Known Member

    Then the arcing time is the remaining assumption. How do address this value?
  13. Zog Well-Known Member

    Opening time is dependant on the mechanical condition of the breaker and will change over time, arcing current is not and depends on the calculatable properties of the system.
  14. stevenal Well-Known Member

    Zog,
    We seem to have a failure to communicate.

    I asked about arcing time, not current. This is the time from initial pole opening until the fault is cleared. (This arc is that which occurs inside the breaker interruption chamber, not the arc flash event at the fault location) Your breaker timing test does not include this piece. How do you account for it? By the scaling of C37.010 Fig.2, the arcing time makes up more than half the interruption time.
    [IMG]
  15. Zog Well-Known Member

    But the opening time is the variable here. I think we are not communicating well, but we are thread jacking. ABB and GE are both using similar technology and there are many white papers on first trip technology available by people more involved in it than I am .
  16. acobb Well-Known Member

    I for one do not think you are thread jacking.....why not go forward and see where it leads?
  17. acobb Well-Known Member

    I also voted for relay time + rated interrupting time. This is based on the interrupting time being the total contact parting plus arcing time.

    Seems to me that the CO requirement is a specific equipment design test.

    If we have to assume the breaker will not operate as advertised, then shouldn't we also assume that the relay won't either....and, if so, where does it end?

    And I have to "ponder" what has happened to the downstream fault once we start the arcing in the breaker?
  18. stevenal Well-Known Member

    Zog,

    I also think this is a worthwhile discussion that should continue. If you consider arcing time to be constant, what constant do you use and where do you get it from?

    I must also question that opening time is the only variable. If first trip measurement finds a slow opening time due to a slow mechanism, the arcing time will also likely be extended as it will take longer to get from contact parting to the point where the arc is extinguished.
  19. Zog Well-Known Member


    Good point about the arcing time, I will have to ask our first trip guru about how they handle that one.
  20. brainfiller Administrator

    I voted breaker and relay time is sufficient since that is what I have done in the past but I am not convinced it is the correct thing to do for arc flash studies. Problem is, I'm not sure what a good answer would be. There is some good info in this thread that I am going to have to ponder.

    This issue was brought up at an IEEE 1584 meeting some time ago,the actual issue was whether to require adding some additional factor to account for age and maintenance for safety. It was only a discussion on the floor but it was discussed and debated but eventually it was decided to just base the clearing time on time current curves / breaker times / induction disc overtravel etc. and if others want to add some additional factor, it is up to them.

    As so many are aware, age, condition and maintenance can have a very large impact. Incident energy is directly proportional to duration so a "hiccup" in a device's operation can create a significant increase in the Ei.

    Good survey question!