PUCKMAN
01-31-2010, 07:11 AM
Does a employee have to be a 'QE' and in ppe to start up a generator online or off line? We test the gen with no load most of the time, sometimes with a load.
Our plant has a 480v 4000a electrical service and the gen is about 1750kw, i believe. Thanks for the responses

Canuck01
01-31-2010, 09:25 AM
:)WAY more information required for this one...

PUCKMAN
02-01-2010, 02:42 PM
like what?

glen1971
03-29-2010, 05:27 AM
Is there an electrician (or QE) when the power goes out and the generator starts? What type of transfer exists? Fault currents/voltages?

Typically most generators connections, transfer switches, buss bars, and the like all are in cabinets.. Unless you start your generator by taking all the doors off the gear, I would say no... Most "start" switches are usually on the front of the Generator Control Panel... This would be the same as turning on/off a light switch... Does your company ask an electrician to be present in the Electrical Rooms, when motors start in the MCCs?

haze10
03-29-2010, 07:20 PM
You should have basic training on the engine, check oil, water, battery, etc - but you don't need to be a Qualified Person to just start and run.