When performing the voltage test on a breaker for LOTO, what energy level is considered?
Case 1: Assume the breaker was inadvertantly left open. You would use the energy level from the load side of the breaker.
Case 2: Assume the breaker failed and one phase stayed closed in and will not open in case of and arc flash. You would use the energy level from the line side of the breaker.
Obviously case 2 is more conservative. I just don't remember NFPA 70E talking about assuming one level of failure in the analysis. It just says to consider the conductor energized until placed in an electrically safe work condition.
Thanks for any insight...